Thread: Example of Over Current Protection Setting using DIgSILENT PowerFactory

  1. #1
    smart
    Guest

    Smile Example of Over Current Protection Setting using DIgSILENT PowerFactory

    This exercise shows how the PF can be used to calculate fault currents and set an overcurrent relay. The coordination graphs will be shown and tripping calculations will be displayed.

    Name:  Fig00.png
Views: 7224
Size:  35.2 KB
    Last edited by smart; 09-04-2010 at 08:34 PM.

  2. #2
    smart
    Guest

    Default Modelling of the network using PowerFactory

    The first setp is to model the network. This is done by creating a new project.

    Name:  Fig01.png
Views: 4908
Size:  4.6 KB
    Last edited by smart; 09-04-2010 at 08:36 PM.

  3. #3
    smart
    Guest

    Default Calculation of Maximum and Minimum Fault Currents

    As known from basic power system theory that the maximum fault current occurs at network when we have three phase fault.
    The figure below shows the result when parameters are defined in the PwerFactory model.

    The maximum fault current = 875 A as expected.

    Name:  Fig02.png
Views: 4851
Size:  7.3 KB

    The minimum fault current = 758 A as expected

    Name:  Fig03.png
Views: 4797
Size:  7.6 KB
    Last edited by smart; 09-04-2010 at 08:37 PM.

  4. #4
    smart
    Guest

    Default

    The next step is to define the protection relay.

    Right click below the transformer and select New Devices -----> Relay Model

    Name:  Fig04.png
Views: 4792
Size:  9.2 KB

    At Relay Type click Select Global Type

    Name:  Fig05.png
Views: 4928
Size:  55.1 KB

    This will take you to library as shown in figure below.
    Choose the following relay as an example in this exercise.
    Other relays can be used if desirable.

    Library ----> Relays ----> Relays ---->
    select then Overcurrent Relays ----> GE Alstom ----> MCGG Series ----> MCGG-22.

    Name:  Fig06.png
Views: 5006
Size:  57.5 KB
    Last edited by smart; 09-04-2010 at 08:40 PM.

  5. #5
    smart
    Guest

    Default

    Now it is time to define the CT for this relay
    Click on Create CT as shown below

    Name:  Fig07.png
Views: 4778
Size:  42.9 KB

    Then choose currnet ratio ----> write 800 A in primary. Click OK

    Name:  Fig08.png
Views: 4828
Size:  100.9 KB
    Last edited by smart; 09-04-2010 at 08:31 PM.

  6. #6
    smart
    Guest

    Default

    Now we need to display the rely using colour.
    Click on colour map as shown below.

    Name:  Fig09.png
Views: 4722
Size:  8.6 KB

    Then from drop down menu select
    Relays, Current and Voltage Transformers as shown

    Name:  Fig10.png
Views: 4737
Size:  45.0 KB

    When you click OK, the SLD shows now the line in Red where relay is connected.

    Name:  Fig11.png
Views: 4712
Size:  4.6 KB

  7. #7
    smart
    Guest

    Default

    We need now to create the graph for the protection devices.

    Right click on the SLD where the relay is connected as sown below.
    Then select Create Time-Overcurrent Plot.

    Name:  Fig12.png
Views: 4730
Size:  11.2 KB

    The log graph appears as another sheet as shown below.

    Name:  Fig13.png
Views: 5016
Size:  14.6 KB

    We can also click right on the graph and add the Transformer Damage Curve as shown.

    Name:  Fig14.png
Views: 4943
Size:  20.3 KB

    Colour of Transformer Damage Curve can be chosen as shown below.

    Name:  Fig15.png
Views: 4827
Size:  95.6 KB

    We can also select the voltage base for displaying the graphs, as shown below.

    Name:  Fig16.png
Views: 4716
Size:  100.3 KB

    There is also of course option to display the fault current (875 A) in different colour (blue)
    and also the tripping time of relay (1.357 s) for that fault current.

    Name:  Fig17.png
Views: 4852
Size:  14.1 KB

  8. #8
    Administrator Admin's Avatar
    Join Date
    Dec 2009
    Location
    Muscat
    Posts
    229
    Blog Entries
    6

    Default Re: Example of Over Current Protection Setting using DIgSILENT PowerFactory

    Thank you for this topic

Thread Information

Users Browsing this Thread

There are currently 8 users browsing this thread. (0 members and 8 guests)

Similar Threads

  1. DIgSILENT StaionWare, The Powerful Protection Management Software
    By Admin in forum StationWare Protection Management Software
    Replies: 1
    Details of Last Post: 06-01-2012, 05:38 PM
  2. DIgSILENT PowerFactory Protection Functions
    By Admin in forum PowerFactory Simulation and Analysis Software
    Replies: 5
    Details of Last Post: 23-02-2010, 09:42 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •